A 240-volt feeder supplying twelve 120-volt, 30A shore power receptacles requires a minimum ampacity of _____ amperes if the demand factor is 80%?

Study for the Load Calculations – Feeders and Services Test. Utilize flashcards and multiple choice questions with hints and explanations. Prepare for your certification!

To determine the minimum ampacity required for a feeder supplying multiple receptacles, you must first consider the demand factor and the total load. In this scenario, you have twelve 120-volt, 30A shore power receptacles.

  1. Calculate the total load: Each receptacle can draw a maximum of 30 amperes at 120 volts. For twelve receptacles, the maximum possible load would be:

[

\text{Total load} = 12 , \text{receptacles} \times 30 , \text{A} = 360 , \text{A}

]

  1. Apply the demand factor: The demand factor is typically a consideration that accounts for the fact that not all devices will be in use simultaneously. In this case, you're given a demand factor of 80%, which means you need to calculate 80% of the total load:

[

\text{Adjusted load} = 360 , \text{A} \times 0.80 = 288 , \text{A}

]

  1. Adjust for feeder capacity: Since this is a 240-volt feeder supplying 120-